Friday January 27th, 2012
Comcast Boot Road Data Center
Agenda
•   8:30-9:00          Breakfast and networking

•   9:00-9:15          Welcome
                       » Logistics
                       » Introductions
                       » Topics for Discussion

•   9:15-10:30         Session One:
                  – New Year, New objectives and priorities…
                  – Vendor Spotlight:
                      » Peter Panfil, Emerson Network Power VP Global Power Sales
                               • Current trends and future challenges
•   10:30-10:40        Break

•   10:40-11:30        Data Center Tour

•   11:30-12:00        Session Two:

                  – User Spotlight: Donna Manley – Post mortem procedures

•   12:00-1:00         Lunch
2012 Goals
• Expansion of data centers
• Audit with RFID
• Bussway
Vendor Spotlight:
       Peter A. Panfil
        VP Global Power Sales
       Emerson Network Power


The State of the Data Center:
 Current trends and future
         challenges
AC Power Technology

DVL DCUG
Jan 2012
Agenda
   Top data center challenges
   Distributed (1+N) and central (N+1) static switch
   Transformer based and transformer free UPS
   Static switches improve MTBF in distribution
   Distribution voltage trends and considerations




                                        COMPANY CONFIDENTIAL   Page 6
Top Data Center Challenges
                                                                       External
                                   Virtualization,                      forces
                                       Cloud                         changing the
                                                                       business
                                                                        climate                    Infrastructure
                  IT Outsourcing                     Consolidation
                                                                                                   Management

                                                                                                   Heat Density
                                                                Efficiency &
      Regulation                                                                  Facility
      Compliance
                                                                   Green                             Availability
                                                                 initiatives     Challenges

                                                                                               Energy Efficiency

                    Higher                             Increasing
                    Density                             Demand                                    Power Density
                                     Reduced
  Business &                          Budget                                                  Source: Data Center Users’ Group
  technology                                                                                  Survey
forces pressing
  on the data
     center


                                                                               COMPANY CONFIDENTIAL               Page 7
Top Data Center Manager Concerns
              Rank Spring 2005         Fall 2007    Spring 2008 Spring 2009        Fall 2009     Spring 2010 Spring 2011
                                                                                                  Monitoring
                    Heat Density     Heat Density Heat Density Heat Density Availability Infrastructure Availability
                1
                       78%                64%            56%            55%            56%           Mgt           53%
                                                                                                     51%
                                                                                    Monitoring                  Monitoring
                       Power             Power          Power          Energy
                                                                                  Infrastructure Heat Density Infrastructure
                2      Density           Density        Density      Efficiency
                                                                                       Mgt           49%           Mgt
                        64%               55%            50%            47%
                                                                                       49%                         52%
                                                                     Monitoring
                                         Energy
                      Availability                    Availability Infrastructure Heat Density Availability Heat Density
                3                      Efficiency
                        57%                              45%            Mgt            46%           47%           47%
                                          39%
                                                                        46%
                                                      Monitoring
                       Space                                                          Energy       Energy         Energy
                                       Availability Infrastructure Availability
                4    Constraints                                                    Efficiency    Efficiency    Efficiency
                                          33%            Mgt            41%
                        32%                                                            40%           44%           44%
                                                         43%
                       Change            Space          Energy         Power          Power        Power          Power
                5   Management        Constraints     Efficiency       Density        Density      Density       Density
                         28%              29%            40%            35%            25%           36%           29%
                      Monitoring       Monitoring
                                                        Space          Space          Space        Space          Space
                    Infrastructure   Infrastructure
                6                                    Constraints Constraints Constraints Constraints Constraints
                         Mgt              Mgt
                                                         26%            29%            25%           21%           18%
                         18%              27%

                      Monitoring / Infrastructure Management properly
                      balances the needs of efficiency and availability
Data Center Users’ Group Survey                                                          COMPANY CONFIDENTIAL                  Page 8
Liebert AC Power
Trends and Strategies
 Trend                                                       Liebert Solution

                                    Liebert APM
               High-Efficiency
                                    Liebert NX
                  Products
                                    Liebert NXL

 Energy
                                    Softscale
Efficiency
             Features Improving     Intelligent Eco Modes
                 Efficiency         TP1 (Energy Star) Rated Distribution Transformers
                                    Distribution Voltages (240/139 and 415/240V)

                  Services          Data Center Power & Cooling Assessments

                                    2 Stage (Segmented) Distribution
                                    400A Panel Boards w/ 100% Rated Mains
Increased     Increasing Power
                                    Busway Solutions
 Density        Requirements
                                    MPX – up to 60A Rack PDU
                                    575V NXL

              Partnerships &        Universal Switchgear Program

 System      Marketing Materials    Large Systems Design Guide
 Focus                              Development of 1+N for Large Systems
               High Availability
                 Topologies         Modular Systems with Internal Redundancy

              Existing Products     Flywheel Systems


Renewable                           Alternative Energy Storage
 Energy                             Solar – ENPC: Solar Controller, EP: Solar
                New Products
                                    Inverter; DOE Funded Smart Grid Research
                                    Wind – ENPC: Wind Converter



                                                                                     COMPANY CONFIDENTIAL   Page 9
High Availability Configurations
         50%            UPS 1     UPS 2    UPS 3     UPS 4            50%          UPS 1    UPS 2    UPS 3    UPS 4

      Utilization                                                  Utilization

                        STS       STS       STS      STS                           STS      STS      STS       STS



                        PDU       PDU       PDU      PDU                           PDU      PDU      PDU       PDU

                                                                                    Interleaved Dual Bus
                             Dual Corded Dual Bus                            Does not require complex switchgear
                    Requires custom switchgear for power tie                       STS does the power tie
                             Maximum Loading N/2                                    Maximum Loading N/2
                     For 4x1000 kVA=2000 kVA Max Load                        For 4x1000 kVA=2000 kVA Max Load


   66%          UPS 1             UPS 2              UPS 3              75%         UPS 1    UPS 2    UPS 3   Reserve

Utilization                                                          Utilization
              STS    STS        STS       STS      STS     STS                      STS       STS      STS




              PDU    PDU        PDU       PDU      PDU       PDU                    PDU       PDU      PDU

                Ring Dual Bus (Distributed Reserve)                               Reserve/Catcher Dual Bus
                Does not require complex switchgear                          Does not require complex switchgear
                      STS does the power tie                                       STS does the power tie
                     Maximum Loading (N-1)/N                                        Maximum Loading N-R
                For 4x1000 kVA=3000 kVA Max Load                             For 4x1000 kVA=3000 kVA Max Load
                                                                                  COMPANY CONFIDENTIAL                  Page 10
Options for parallel redundant UPS


     UPS          UPS     UPS
     Core         Core                           UPS      UPS     UPS
                          Core
                                                 Core     Core    Core    STS
       SS          SS         SS




    Paralleling Cabinet                          System Control Cabinet

                                   IT Load                                      IT Load



       Distributed Bypass (1+N)                         Central Bypass (N+1)
Distributed static switches                  Centralized static transfer switch
Individual modules manage load transfers     System-level control, fault tolerant
Cannot parallel different sized UPS          Size of STS determines total capacity


                                                        COMPANY CONFIDENTIAL              Page 11
N+1 vs 1+N
   For a system of 4x750kVA
     –   1+N will cost $1.2M , max aic 100kaic
     –   N+1 will cost $1.4M , max aic 200kaic
     –   If specifications allow both the 1+N will always be cheaper
   When operating on inverter both have identical performance
     –   N+1 has better fault transfer to bypass due to one 3000/4000amp breaker
     –   1+N has more sag due to parallel SS/inductors/1200a CB during fault transfer.
     –   Since MTBF of NXL module is 200,000 hours the 4 module system will transfer to
         bypass every 50,000 hr or 6 years if capacity and statistically never if redundant
   1+N since it is composed of SMS can easily be split and sent to different
    locations
     –   Requires two upstream feeder breakers or single input kit versus one for N+1
   NEC70E requires both to have downstream ROB to be able to service
    one module while system is energized



                                                           COMPANY CONFIDENTIAL       Page 12
Transformer Based UPS System
            Single Module, Topology Three-Line
AC
                                                                                                                                                        Output
     FBO                                                                                                                                MBB
                                                                                 BIB
             Bypass can be connected to                                                                                            EG
                                                                                                                                              MIB
               separate utility source

                Input
                             12P isolated
              Isolation
                                                                                                 3P
                      A                                                                    BFB


AC
                CB1

      FBO
                                                                                                                              E
                   Trap
                Disconnect
                                                                                                                             CB2
                                                                                                            N                N
                                                                                                                     MBJ
                                                                                                                             EG

                                     or                                                                                              Neutral-Gnd
                             12P non isolated                                 Output                  GEC
                                                                                                                                    Management;
                                   Battery and   To Batteries
                                                                             Isolation                                              Low Common
                                     DC Bus
                                                                                                                                    Mode Noise;
                                    Isolation             Positive
                                                          DC bus

                                                                     +   +   +                                                        Separately
                                                                                                                                       Derived
                                                                                                                                        Source
                                                                     +   +   +




                                                                                                                Output -AC

                                                          Negative
                                                          DC bus




                                                                                       COMPANY CONFIDENTIAL                                   Page 13
Transformer Less UPS System
   Single Module, Topology Three-Line



   Some topologies require the        Less Eff     High
    bypass to be connected to         Rectifier   DC Bus
     the same utility source



                                                                                   No Output
                                                                                    Isolation




No Input
                      Additional DC                         Neutral Mgt /
Isolation
                       Converter                           Control Required
                                                            COMPANY CONFIDENTIAL    Page 14
Application Philosophy
Transformer Based & Transformer Free UPS
   There are appropriate applications for both transformer
    based and transformer free UPS
    – Many customers have multiple applications with different priorities
   Transformer based enterprise UPS’s offer the highest
    availability
    – Galvanic isolation is provided for DC fault protection
    – Output isolation protects the critical load and simplifies fault
      management
    – Use ultra-reliable, efficient SCR-based rectifiers and simple lower
      voltage inverters
    – Can feed rectifier and bypass from dual Separately Derived Sources
    – Inherently compatible with High Resistance Grounded systems
   Transformer-free UPS’s offer low TCO with high
    availability
    – Double conversion efficiency up to 96%
    – Uniformly Low input harmonics with consistent high power factor.
    – Power distribution provides complete solution for transformer free UPS
                                                  COMPANY CONFIDENTIAL      Page 15
Transformer Based –vs-
    Transformer Free Design
Characteristic                       Transformer Free          Transformer Based

AC-AC Double Conversion Efficiency   96% Range                 94% Range

Eco Mode Efficiency                  Up to 99%                 Up to 99%

Ground Fault Protection Coordination External or Incremental   Inherent

Arc Flash Mitigation                 External or Incremental   Inherent

> 480 volt ratings for high power Additional External          No Additional External
density                           Xformers Required            Xformers Needed
Reduction in Common mode noise       No                        Yes
and EMI
Rectifier Resiliency IGBT vs. SCR    Lower                     Higher

High Resistance Ground               No                        Yes
Compatibility


                                                        COMPANY CONFIDENTIAL      Page 16
System MTBF
Without Static Switches
                                                                 Module Demonstrated MTBF Block Diagram
Tier 3-4 UPS Power configuration into a Dual Input IT Load


                                           MTBF UPS Out = UPS 1 = UPS2
Primary AC Input MTBF =                    S10 UPS MTBF out = > 1.6M hr MTBF                 Field Observed
Bypass AC Input =
          100 Hr MTBF

       Bypass AC Input                                                                           PDU MTBF > 9 M hr
                                         UPS 1                                                               Field-Observed
       Primary AC Input                   SMS                MTBF > 1.7 M hr                       PDU




                                                                                           IT each AC Input MTBF =
                                                                                   Simplified - Components in series
                                                                               = 1/((1/MTBF UPS) + (1/MTBF PDU))          IT Load
                                                                                                  MTBF = 1.4 M hr




       Primary AC Input                                                                            PDU
                                         UPS 2
       Bypass AC Input                    SMS




                                                                                  COMPANY CONFIDENTIAL                   Page 17
System MTBF
Improvement With Static Switches
                                                                        Module Demonstrated MTBF Block Diagram
Tier 3-4 UPS Power configuration with STS 2 into a Dual Input IT Load


                                            MTBF UPS Out = UPS 1 = UPS2
Primary AC Input MTBF =                     S10 UPS MTBF out = > 1.6M hr MTBF                           Field Observed
Bypass AC Input =
          100 Hr MTBF

       Bypass AC Input                                                       STS MTBF > 7.2 M hr            PDU MTBF > 9 M hr
                                             UPS 1         MTBF > 1.7 M hr                                              Field-Observed
       Primary AC Input                       SMS                               STS2                          PDU

                  enter
   UPS MTBF = 1.7
                        Combined MTBF of two                              STS 2 Field-Observed MTBF:
                        Paralleled UPS outputs                            Field-observed STS MTFB output
       = MTBF1+MTBF2+((MTBF1*MTBF2)/(MTTR))                               ≈ 7.2 M hr MTBF                                            IT Load
                            MTBF = 113,441 M hr                                                       IT each AC Input MTBF =
                                                                                              Simplified - Components in series
    where Mean Time to Repair [MTTR] =            24 hrs                  = 1/((1/Para UPS Out) + 1/MTBF STS) + (1/MTBF PDU))
    where UPS repair is less than 8 hrs       enter                                                          MTBF = 4.0 M hr


       Primary AC Input                                                         STS2                          PDU
                                             UPS 2
       Bypass AC Input                        SMS




                                                                                           COMPANY CONFIDENTIAL                     Page 18
Traditional Dual Bus, 2N
                                                                              Precision
                                                            Engine             Cooling
                                                           Generators



                                                            Generator                     Feed to
                              Service     Surge                             Input
                                                            Paralleling
                               Feed     Suppression
                                                            Switchgear
                                                                          Switchgear       UPS
          UPS A
           Primary




                                                                                                       Alternate
                       STS2
                                                                                             STS2


    LBS


                           PDU:   RDC/                                     RDC/
           Alternate




                                                          Racks                 PDU:




                                                                                                    Primary
                          PPC/FPC FDC                                      FDC PPC/FPC
                                                      Multiple Rows
          UPS B

                 Dual Bus = twice as many power cables
                                                                 COMPANY CONFIDENTIAL          Page 19
Distribution Voltages
           600VAC   •UPS      600V        •PDU        208/120V          •Rack



           480VAC   •UPS      480V        •PDU        208/120V          •Rack
Today




           415VAC   •UPS    415/240V      •RDC         415/240V         •Rack



           480VAC   •UPS    480/277V      •RDC        480/277V          •Rack




           600VAC   •UPS      600V        •PDU           415V           •Rack
Emerging




           480VAC   •UPS    415/240V      •RDC         415/240V         •Rack

                    Efficiency improvement ???
                                                 COMPANY CONFIDENTIAL   Page 20
Isolation Transformers At The PDU
PROS
   Single point ground, separately derived source with
    safety ground closer to the load reduces susceptibility to
    lightning and other transients
   Only requires a 3 wire system to the PDU input
   Provide impedance which reduces available fault currents
    ~ and Arc Flash potential at distribution points
CONS
   Size – PDU’s with transformers can be larger
   Transformation losses …However…today’s TP-1
    transformers are typically 98.5% + efficient
   Higher weight and cost

                                        COMPANY CONFIDENTIAL   Page 21
PDU Transformer Efficiency
                99.00
                                  $$$

                98.50
 % EFFICIENCY




                98.00                                      300 kVA K20
                                                           300 kVA STD
                97.50
                                                           300 kVA K20 TP1
                97.00                                      300 kVA STD TP1


                96.50

                96.00
                        15% 25% 35% 50% 65% 75% 100%
                                  % LOAD

                                               COMPANY CONFIDENTIAL   Page 22
A Fresh Look at the 400-415v System
   Modern Power supplies are wide ranging 208v to 240v test
     – Higher voltage equates to higher efficiency – about 0.3% gain
   Line to neutral connection – 230/400 or 240/415v
     – Can be transformer free saving energy-1-3% gain, plus cooling savings
     – Fault current HAS been a major concern if transformer free
           • 480 or 600v to 240/415 v with Auto (efficiency) or Iso. (aic and N-G)
           • Historically, vendors supplied pieces and parts, but not an end-to-
             end solution for 400-415V in North America.
     – Neutral fault path and neutral noise are concerns with transformer free
     – No Rack PRU balancing issue
   Line to Line connection – 120/208 and 127/240v
     – New copper TP-1 Transformers have 1.5% losses
     – Fault current is controlled by the transformer
           • Panels, breakers, power cords, rack PDU and servers rated for fault
             current (aic) are readily available
     – Neutral fault path and neutral noise are from server to isolation
         transformer only

                                                     COMPANY CONFIDENTIAL    Page 23
Short Circuit Considerations (Historical)
Panelboards
   208/120 & 240/139 Volt Panels
    Rated at 250V
     –   Type NQ
     –   Available to 22kAIC
   480/277 & 415/240 Requires
    Panels Rated to 600V
     –   Type NF
     –   Series rated with main CB at
          •   35,65 and 100kaic

     –   Physically larger
     –   More costly (10-25%)

Are your Rack PDUs and
servers rated for this high AIC?
                                        COMPANY CONFIDENTIAL   Page 24
Fault Current
Arc Flash Considerations
   Arc flash?
     – Bolted vs. arcing faults
     – Significant incident energy released during the arcing event and is
       considered the “arc flash hazard”
   NFPA 70E-2004 “A flash hazard analysis be done in order to protect
    personnel from the possibility of being injured by an arc flash”
   Determination of required PPE - Personal Protective Equipment
   Calculation of incidence of energy
     – Ampere rating of over current protective device
     – Operating time of the device
     – Available fault current is key!!!




                                                   COMPANY CONFIDENTIAL      Page 25
Solving the 415V AIC Issue
                                                                                Problem
    3250 kVA                               3250 kVA                           • AC Distribution panels
    34.5 kV –                              34.5 kV –                               • Lighting panels
    480/277                                415/240
    Z >= 5.32%       X                     Z >= 5.32%       X                      • Exposed buss (arch flash)
                          Isc ~ 73,480A                          Isc ~ 84,989A     • AIC of UL approved “touch
                                                                                   safe”
                                                                              • Rack PDUs
                   UPS                                    UPS                      • AIC may exceed safe design
                 SYSTEM                                 SYSTEM
                                                                                Solutions
                                                                                • Introduce impedance such as
                                                                                inductor or transformer
                                                                                       •Disadvantage efficiency
                                                                                       •Advantage grounding and
                                                                                       fault management (tx)
                                                                                • I-Line Panels offer higher AIC
300 kVA
480V –                                                                          (100k) and safer design
208/120V
            PDU                                    PDU                          • Higher AIC capable RPDU’s
Z >= 4%
                 X                                      X
                          Isc ~ 17,576 A                         Isc ~ 56,144 A
           RACK                                   RACK
                         Isc < 5kA                              Isc ~ 10-12kA
      208 Volt                              415 Volt
     Distribution                          Distribution
                                                                         COMPANY CONFIDENTIAL             Page 26
Distribution Voltage Considerations
UPS System Voltage and Capacity

5000 Amp System                     UPS System Voltage
                             415V          480V                 600V
Max. Bus Capacity          3590 kVA      4152 kVA         5190 kVA


   Maximize your investment in breakers and gear with
    higher UPS System voltages
   The higher the chosen voltage - the greater the potential
    capacity – 15% to 25%




                                         COMPANY CONFIDENTIAL      Page 27
Distribution Voltage Pros & Cons
                                     PROS                                         CONS
                   Most commonly accepted application            2-3% transformation energy loss
480 – 208/120      Reduced aic – fault curent                    208V requires 2 pole breaker
                   Uses standard 240V panelboard & breakers      Reduces the number of poles
600 – 208/120      N-G bond at PDU
                   N-G bond at PDU( iso)                         0.5 to 1.3%% transformer energy loss
480 – 400/230      Higher energy efficiency                      Can’t power 120V equipment
                   Higher energy density                         More circuits due to1-pole
600 – 400/230      Higher UPS capacity - kVA                     N-G bond (auto) at service entrance
                   Reduced AIC – fault current
                   No transformation energy losses               Can’t power 120V or 240V equipment
 480 – 480         No neutral required (unless 277V loads)       Requires 480V panelboard & breakers
                                                                  Few servers at 480V & 277V
480 – 480/277                                                     Higher AIC – fault current at load
                   No transformation energy losses               N-G bond at bypass transformer
                   240V load requires 1 pole breaker             Requires 480V panelboard& breakers
480 – 415/240      More useable pole spaces                      Requires UPS Maint Bypass Xfmr
                   Higher energy efficiency                      Higher AIC – fault current at load
                   No transformation energy losses               Can’t power 120V equipment
                   Reduced cooling load                          Requires 480V panelboard& breakers
                   240V load requires 1 pole breaker             Needs different approach to fault
415 – 415/240      More useable pole spaces                       current management
                   Higher energy efficiency                      N-G bond at service entrance
                   Save cost and weight of transformers in       Increase cost of full neutral and higher
                    PDUs                                           ampacity – lower system kVA


                                                               COMPANY CONFIDENTIAL               Page 28
29
     COMPANY CONFIDENTIAL   Page 29 29
Liebert STS2, S610, NXb, PPC, FPC,
NXL Reliability Summary May 2011
Product          Operating Hours          Mod. MTBF         Sys. MTBF

(Cur # Units)    Oct 00 – Mar 11          Code 14           Code 15

                     Transfer To Bypass   Unfiltered        Filtered
                                                Critical Bus Failure
STS 2 (4,082)    121,462,656 Hrs.           886,589 Hrs.    8,675,904 Hrs.

S610 (6,642)     419,488,584 Hrs.            47,838 Hrs.    1,712,198 Hrs.

NXb (2,843)      105,092,280 Hrs.           202,490 Hrs.    2,563,226 Hrs.

PPC (10,474)      878,674,536 Hrs.        2,670,743 Hrs.   10,217,146 Hrs.

FPC (1,951)         41,363,976 Hrs.       10,340,994 Hrs. 13,787,992 Hrs.

NXL (612)             5,581,704 Hrs.        206,730 Hrs.   1,395,426 Hrs.*

APM (113)                384,432 Hrs.       384,432 Hrs.      384,432 Hrs.
                * Updated Nov 2011              COMPANY CONFIDENTIAL    Page 30 30
Power Business Segments
                                    Primary Motivation
Critical                                                           TCO
Infrastructure    Availability                                                                 Capital/Operational Savings
                                                                                          Capital/Operational Savings
                   Availability

                  Core Enterprise                                                                           Scale-Out
 Customer
                          Traditionalist                  Opportunist                       Experimentalist
   Type
                                                     Operates on the edge of
                 Firmly adheres to long-held,                                          Ventures outside of industry
Customer                                               acceptable operating
                 proven industry standards to                                         standards and best-practices
Behavior &                                           recommendations taking
                    maximize infrastructure                                            with the goal to significantly
Motivation                                          calculated risks to balance
                          availability                                                    reduce financial costs
                                                  financial costs and availability

  Primary        Transformer Based          Transformer Based           Transformer Free          Battery on Server
Technology              UPS                  UPS in Eco-Mode            UPS in Eco-Mode                 Model
                                           Transformer Free UPS

                 • Providing mission critical    • Providing less critical           • Customers still expect
                   computing to customers          computing to internal or            application high availability
                 • Required uptime based on        external customers                • Basic services are provided
Customer
                   government regulations        • Need to meet customer SLAs          for limited fees with no
Attributes
                 • Extremely high cost of          for uptime with limited             guarantees
                   application downtime            penalties                         • High compute volume
                                                 • Balancing cost of downtime          demands lowest computing
                                                   with OPEX                           costs possible
                                                                             COMPANY CONFIDENTIAL                Page 31
High Availability Configurations
         50%            UPS 1     UPS 2    UPS 3     UPS 4            50%          UPS 1    UPS 2    UPS 3    UPS 4

      Utilization                                                  Utilization

                        STS       STS       STS      STS                           STS      STS      STS       STS



                        PDU       PDU       PDU      PDU                           PDU      PDU      PDU       PDU

                                                                                    Interleaved Dual Bus
                             Dual Corded Dual Bus                            Does not require complex switchgear
                    Requires custom switchgear for power tie                       STS does the power tie
                             Maximum Loading N/2                                    Maximum Loading N/2
                     For 4x1000 kVA=2000 kVA Max Load                        For 4x1000 kVA=2000 kVA Max Load


   66%          UPS 1             UPS 2              UPS 3              75%         UPS 1    UPS 2    UPS 3   Reserve

Utilization                                                          Utilization
              STS    STS        STS       STS      STS     STS                      STS       STS      STS




              PDU    PDU        PDU       PDU      PDU       PDU                    PDU       PDU      PDU

                Ring Dual Bus (Distributed Reserve)                               Reserve/Catcher Dual Bus
                Does not require complex switchgear                          Does not require complex switchgear
                      STS does the power tie                                       STS does the power tie
                     Maximum Loading (N-1)/N                                        Maximum Loading N-R
                For 4x1000 kVA=3000 kVA Max Load                             For 4x1000 kVA=3000 kVA Max Load
                                                                                  COMPANY CONFIDENTIAL                  Page 32
Break:
See you in 15!
User Spotlight: Donna
        Manley
Post mortem procedures
Managing a Full Data Center
      Power Down


          Donna M. Manley, MBA
  IT Senior Director, Computer Operations
         University of Pennsylvania
July 3-4, 2009




      36
July 3-4, 2009




      37
January 2010 (Morning)




          38
January 2010 (Noon)




         39
40
Before you get started….


•    Agree upon scope
•    Documentation
•    Validate infrastructure and architecture
•    Asset identification and application dependencies
•    Understand what pre-work can be completed
•    DR site and Vital Records storage providers on standby
•    What’s the weather forecast?

    Take the opportunity to do stuff you wouldn’t normally be able to
                            without an outage!



                                   41
42
43
44
Logistics….


•   Coordination with Public Safety
•   Coordination with Facilities
•   Command Center
•   Know who will be there and when
•   Vendor Expectations
•   Accommodations, food, and beverage




                              45
46
47
Managing the Outage…


•   Communication (Bridges, Web, Email)
•   Playbook
•   Change Freeze
•   Action Items to be remediated prior
•   Test plan
•   Points of Contact - Data Center/Facilities/Vendors
•   Who gives the “GO”




                                 48
49
50
51
Post Outage…


•   Communication (Bridges, Web, Email)
•   Execute Test Plan
•   Lessons Learned
•   Process and procedural modifications
•   Automation opportunities
•   Sleep!



    Lots of great information was compiled for this event – keep it
                                current!


                                  52
Thank you for allowing me to
      share my thoughts with you
                today!


Donna M. Manley, MBA
IT Sr. Director, Computer Operations
ITIL V3 Foundations Certified
University of Pennsylvania
manleydm@isc.upenn.edu
                                       53
Survey
  – Was this forum beneficial?
  – Was this the proper number of end users or
    should the forum grow? If grow, please give a
    number you feel would be appropriate.
  – How often should this forum meet? When?
  – What topics would you be interested in
    discussing at the next meeting?
  – What other venues for this event would you like
    to see?
Thank you for
 attending!

Weitere ähnliche Inhalte

Ähnlich wie PowerPoint from January 27th 2012 Forum

Top 5 Ways the Cloud is Impacting Your IT
Top 5 Ways the Cloud is Impacting Your ITTop 5 Ways the Cloud is Impacting Your IT
Top 5 Ways the Cloud is Impacting Your ITValencell, Inc.
 
The Importance of Data Transparency in Smart Grids
The Importance of Data Transparency in Smart GridsThe Importance of Data Transparency in Smart Grids
The Importance of Data Transparency in Smart Gridshsvenu
 
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...Vlerick_Alumni
 
Accelerating the Speed of Innovation - Jason Waxman, Intel
Accelerating the Speed of Innovation - Jason Waxman, IntelAccelerating the Speed of Innovation - Jason Waxman, Intel
Accelerating the Speed of Innovation - Jason Waxman, IntelOpen Data Center Alliance
 
Cloud Computing
Cloud ComputingCloud Computing
Cloud ComputingFonality
 
Cloud services zimbabwe
Cloud services   zimbabweCloud services   zimbabwe
Cloud services zimbabweTechZim
 
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...Scott Bils
 
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...Everest Group
 
Service Availability and Performance Management - PCTY 2011
Service Availability and Performance Management - PCTY 2011Service Availability and Performance Management - PCTY 2011
Service Availability and Performance Management - PCTY 2011IBM Sverige
 
The New Network for the Data Center
The New Network for the Data CenterThe New Network for the Data Center
The New Network for the Data CenterJuniper Networks
 
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Newlink
 
Thenewnetworkforthedatacenter 100519185534-phpapp02
Thenewnetworkforthedatacenter 100519185534-phpapp02Thenewnetworkforthedatacenter 100519185534-phpapp02
Thenewnetworkforthedatacenter 100519185534-phpapp02Newlink
 
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Newlink
 
Enhancing Facility Performance | Maximizing Investments | Reducing Utility
Enhancing Facility Performance | Maximizing Investments | Reducing UtilityEnhancing Facility Performance | Maximizing Investments | Reducing Utility
Enhancing Facility Performance | Maximizing Investments | Reducing UtilityCenter for Sustainable Energy
 
Keynote 中国云计算调查报告-alter-埃森哲
Keynote 中国云计算调查报告-alter-埃森哲Keynote 中国云计算调查报告-alter-埃森哲
Keynote 中国云计算调查报告-alter-埃森哲Riquelme624
 
Keynote 中国云计算调查报告 alter 埃森哲
Keynote 中国云计算调查报告 alter 埃森哲Keynote 中国云计算调查报告 alter 埃森哲
Keynote 中国云计算调查报告 alter 埃森哲Riquelme624
 
A View From the CIO's Driver Seat
A View From the CIO's Driver SeatA View From the CIO's Driver Seat
A View From the CIO's Driver SeatJuniper Networks
 
The True Value of Grid Reliability
The True Value of Grid ReliabilityThe True Value of Grid Reliability
The True Value of Grid ReliabilityEchelon Corporation
 

Ähnlich wie PowerPoint from January 27th 2012 Forum (20)

Top 5 Ways the Cloud is Impacting Your IT
Top 5 Ways the Cloud is Impacting Your ITTop 5 Ways the Cloud is Impacting Your IT
Top 5 Ways the Cloud is Impacting Your IT
 
The Importance of Data Transparency in Smart Grids
The Importance of Data Transparency in Smart GridsThe Importance of Data Transparency in Smart Grids
The Importance of Data Transparency in Smart Grids
 
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...
Thomas Van Maele, Partner Corporate Finance, Econopolis (Market structure and...
 
Accelerating the Speed of Innovation - Jason Waxman, Intel
Accelerating the Speed of Innovation - Jason Waxman, IntelAccelerating the Speed of Innovation - Jason Waxman, Intel
Accelerating the Speed of Innovation - Jason Waxman, Intel
 
Sgcp12 faulkner-cal
Sgcp12 faulkner-calSgcp12 faulkner-cal
Sgcp12 faulkner-cal
 
Cloud Computing
Cloud ComputingCloud Computing
Cloud Computing
 
Cloud services zimbabwe
Cloud services   zimbabweCloud services   zimbabwe
Cloud services zimbabwe
 
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...
Enterprise Cloud Stakeholders Speak: Adoption Patterns, Barriers & Post-Adopt...
 
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...
The Enterprise Business Case for Cloud Transformation: Introducing Everest Gr...
 
DCIM
DCIMDCIM
DCIM
 
Service Availability and Performance Management - PCTY 2011
Service Availability and Performance Management - PCTY 2011Service Availability and Performance Management - PCTY 2011
Service Availability and Performance Management - PCTY 2011
 
The New Network for the Data Center
The New Network for the Data CenterThe New Network for the Data Center
The New Network for the Data Center
 
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
 
Thenewnetworkforthedatacenter 100519185534-phpapp02
Thenewnetworkforthedatacenter 100519185534-phpapp02Thenewnetworkforthedatacenter 100519185534-phpapp02
Thenewnetworkforthedatacenter 100519185534-phpapp02
 
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
Thenewnetworkforthedatacenter 100519185534-phpapp02 (1)
 
Enhancing Facility Performance | Maximizing Investments | Reducing Utility
Enhancing Facility Performance | Maximizing Investments | Reducing UtilityEnhancing Facility Performance | Maximizing Investments | Reducing Utility
Enhancing Facility Performance | Maximizing Investments | Reducing Utility
 
Keynote 中国云计算调查报告-alter-埃森哲
Keynote 中国云计算调查报告-alter-埃森哲Keynote 中国云计算调查报告-alter-埃森哲
Keynote 中国云计算调查报告-alter-埃森哲
 
Keynote 中国云计算调查报告 alter 埃森哲
Keynote 中国云计算调查报告 alter 埃森哲Keynote 中国云计算调查报告 alter 埃森哲
Keynote 中国云计算调查报告 alter 埃森哲
 
A View From the CIO's Driver Seat
A View From the CIO's Driver SeatA View From the CIO's Driver Seat
A View From the CIO's Driver Seat
 
The True Value of Grid Reliability
The True Value of Grid ReliabilityThe True Value of Grid Reliability
The True Value of Grid Reliability
 

Kürzlich hochgeladen

Design pattern talk by Kaya Weers - 2024 (v2)
Design pattern talk by Kaya Weers - 2024 (v2)Design pattern talk by Kaya Weers - 2024 (v2)
Design pattern talk by Kaya Weers - 2024 (v2)Kaya Weers
 
Digital Identity is Under Attack: FIDO Paris Seminar.pptx
Digital Identity is Under Attack: FIDO Paris Seminar.pptxDigital Identity is Under Attack: FIDO Paris Seminar.pptx
Digital Identity is Under Attack: FIDO Paris Seminar.pptxLoriGlavin3
 
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotes
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotesMuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotes
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotesManik S Magar
 
The State of Passkeys with FIDO Alliance.pptx
The State of Passkeys with FIDO Alliance.pptxThe State of Passkeys with FIDO Alliance.pptx
The State of Passkeys with FIDO Alliance.pptxLoriGlavin3
 
Testing tools and AI - ideas what to try with some tool examples
Testing tools and AI - ideas what to try with some tool examplesTesting tools and AI - ideas what to try with some tool examples
Testing tools and AI - ideas what to try with some tool examplesKari Kakkonen
 
Generative AI - Gitex v1Generative AI - Gitex v1.pptx
Generative AI - Gitex v1Generative AI - Gitex v1.pptxGenerative AI - Gitex v1Generative AI - Gitex v1.pptx
Generative AI - Gitex v1Generative AI - Gitex v1.pptxfnnc6jmgwh
 
TrustArc Webinar - How to Build Consumer Trust Through Data Privacy
TrustArc Webinar - How to Build Consumer Trust Through Data PrivacyTrustArc Webinar - How to Build Consumer Trust Through Data Privacy
TrustArc Webinar - How to Build Consumer Trust Through Data PrivacyTrustArc
 
Time Series Foundation Models - current state and future directions
Time Series Foundation Models - current state and future directionsTime Series Foundation Models - current state and future directions
Time Series Foundation Models - current state and future directionsNathaniel Shimoni
 
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24Mark Goldstein
 
So einfach geht modernes Roaming fuer Notes und Nomad.pdf
So einfach geht modernes Roaming fuer Notes und Nomad.pdfSo einfach geht modernes Roaming fuer Notes und Nomad.pdf
So einfach geht modernes Roaming fuer Notes und Nomad.pdfpanagenda
 
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024BookNet Canada
 
QCon London: Mastering long-running processes in modern architectures
QCon London: Mastering long-running processes in modern architecturesQCon London: Mastering long-running processes in modern architectures
QCon London: Mastering long-running processes in modern architecturesBernd Ruecker
 
Glenn Lazarus- Why Your Observability Strategy Needs Security Observability
Glenn Lazarus- Why Your Observability Strategy Needs Security ObservabilityGlenn Lazarus- Why Your Observability Strategy Needs Security Observability
Glenn Lazarus- Why Your Observability Strategy Needs Security Observabilityitnewsafrica
 
A Deep Dive on Passkeys: FIDO Paris Seminar.pptx
A Deep Dive on Passkeys: FIDO Paris Seminar.pptxA Deep Dive on Passkeys: FIDO Paris Seminar.pptx
A Deep Dive on Passkeys: FIDO Paris Seminar.pptxLoriGlavin3
 
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...Wes McKinney
 
Modern Roaming for Notes and Nomad – Cheaper Faster Better Stronger
Modern Roaming for Notes and Nomad – Cheaper Faster Better StrongerModern Roaming for Notes and Nomad – Cheaper Faster Better Stronger
Modern Roaming for Notes and Nomad – Cheaper Faster Better Strongerpanagenda
 
Abdul Kader Baba- Managing Cybersecurity Risks and Compliance Requirements i...
Abdul Kader Baba- Managing Cybersecurity Risks  and Compliance Requirements i...Abdul Kader Baba- Managing Cybersecurity Risks  and Compliance Requirements i...
Abdul Kader Baba- Managing Cybersecurity Risks and Compliance Requirements i...itnewsafrica
 
TeamStation AI System Report LATAM IT Salaries 2024
TeamStation AI System Report LATAM IT Salaries 2024TeamStation AI System Report LATAM IT Salaries 2024
TeamStation AI System Report LATAM IT Salaries 2024Lonnie McRorey
 
Emixa Mendix Meetup 11 April 2024 about Mendix Native development
Emixa Mendix Meetup 11 April 2024 about Mendix Native developmentEmixa Mendix Meetup 11 April 2024 about Mendix Native development
Emixa Mendix Meetup 11 April 2024 about Mendix Native developmentPim van der Noll
 
A Journey Into the Emotions of Software Developers
A Journey Into the Emotions of Software DevelopersA Journey Into the Emotions of Software Developers
A Journey Into the Emotions of Software DevelopersNicole Novielli
 

Kürzlich hochgeladen (20)

Design pattern talk by Kaya Weers - 2024 (v2)
Design pattern talk by Kaya Weers - 2024 (v2)Design pattern talk by Kaya Weers - 2024 (v2)
Design pattern talk by Kaya Weers - 2024 (v2)
 
Digital Identity is Under Attack: FIDO Paris Seminar.pptx
Digital Identity is Under Attack: FIDO Paris Seminar.pptxDigital Identity is Under Attack: FIDO Paris Seminar.pptx
Digital Identity is Under Attack: FIDO Paris Seminar.pptx
 
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotes
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotesMuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotes
MuleSoft Online Meetup Group - B2B Crash Course: Release SparkNotes
 
The State of Passkeys with FIDO Alliance.pptx
The State of Passkeys with FIDO Alliance.pptxThe State of Passkeys with FIDO Alliance.pptx
The State of Passkeys with FIDO Alliance.pptx
 
Testing tools and AI - ideas what to try with some tool examples
Testing tools and AI - ideas what to try with some tool examplesTesting tools and AI - ideas what to try with some tool examples
Testing tools and AI - ideas what to try with some tool examples
 
Generative AI - Gitex v1Generative AI - Gitex v1.pptx
Generative AI - Gitex v1Generative AI - Gitex v1.pptxGenerative AI - Gitex v1Generative AI - Gitex v1.pptx
Generative AI - Gitex v1Generative AI - Gitex v1.pptx
 
TrustArc Webinar - How to Build Consumer Trust Through Data Privacy
TrustArc Webinar - How to Build Consumer Trust Through Data PrivacyTrustArc Webinar - How to Build Consumer Trust Through Data Privacy
TrustArc Webinar - How to Build Consumer Trust Through Data Privacy
 
Time Series Foundation Models - current state and future directions
Time Series Foundation Models - current state and future directionsTime Series Foundation Models - current state and future directions
Time Series Foundation Models - current state and future directions
 
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24
Arizona Broadband Policy Past, Present, and Future Presentation 3/25/24
 
So einfach geht modernes Roaming fuer Notes und Nomad.pdf
So einfach geht modernes Roaming fuer Notes und Nomad.pdfSo einfach geht modernes Roaming fuer Notes und Nomad.pdf
So einfach geht modernes Roaming fuer Notes und Nomad.pdf
 
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024
New from BookNet Canada for 2024: Loan Stars - Tech Forum 2024
 
QCon London: Mastering long-running processes in modern architectures
QCon London: Mastering long-running processes in modern architecturesQCon London: Mastering long-running processes in modern architectures
QCon London: Mastering long-running processes in modern architectures
 
Glenn Lazarus- Why Your Observability Strategy Needs Security Observability
Glenn Lazarus- Why Your Observability Strategy Needs Security ObservabilityGlenn Lazarus- Why Your Observability Strategy Needs Security Observability
Glenn Lazarus- Why Your Observability Strategy Needs Security Observability
 
A Deep Dive on Passkeys: FIDO Paris Seminar.pptx
A Deep Dive on Passkeys: FIDO Paris Seminar.pptxA Deep Dive on Passkeys: FIDO Paris Seminar.pptx
A Deep Dive on Passkeys: FIDO Paris Seminar.pptx
 
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...
The Future Roadmap for the Composable Data Stack - Wes McKinney - Data Counci...
 
Modern Roaming for Notes and Nomad – Cheaper Faster Better Stronger
Modern Roaming for Notes and Nomad – Cheaper Faster Better StrongerModern Roaming for Notes and Nomad – Cheaper Faster Better Stronger
Modern Roaming for Notes and Nomad – Cheaper Faster Better Stronger
 
Abdul Kader Baba- Managing Cybersecurity Risks and Compliance Requirements i...
Abdul Kader Baba- Managing Cybersecurity Risks  and Compliance Requirements i...Abdul Kader Baba- Managing Cybersecurity Risks  and Compliance Requirements i...
Abdul Kader Baba- Managing Cybersecurity Risks and Compliance Requirements i...
 
TeamStation AI System Report LATAM IT Salaries 2024
TeamStation AI System Report LATAM IT Salaries 2024TeamStation AI System Report LATAM IT Salaries 2024
TeamStation AI System Report LATAM IT Salaries 2024
 
Emixa Mendix Meetup 11 April 2024 about Mendix Native development
Emixa Mendix Meetup 11 April 2024 about Mendix Native developmentEmixa Mendix Meetup 11 April 2024 about Mendix Native development
Emixa Mendix Meetup 11 April 2024 about Mendix Native development
 
A Journey Into the Emotions of Software Developers
A Journey Into the Emotions of Software DevelopersA Journey Into the Emotions of Software Developers
A Journey Into the Emotions of Software Developers
 

PowerPoint from January 27th 2012 Forum

  • 1. Friday January 27th, 2012 Comcast Boot Road Data Center
  • 2. Agenda • 8:30-9:00 Breakfast and networking • 9:00-9:15 Welcome » Logistics » Introductions » Topics for Discussion • 9:15-10:30 Session One: – New Year, New objectives and priorities… – Vendor Spotlight: » Peter Panfil, Emerson Network Power VP Global Power Sales • Current trends and future challenges • 10:30-10:40 Break • 10:40-11:30 Data Center Tour • 11:30-12:00 Session Two: – User Spotlight: Donna Manley – Post mortem procedures • 12:00-1:00 Lunch
  • 3. 2012 Goals • Expansion of data centers • Audit with RFID • Bussway
  • 4. Vendor Spotlight: Peter A. Panfil VP Global Power Sales Emerson Network Power The State of the Data Center: Current trends and future challenges
  • 5. AC Power Technology DVL DCUG Jan 2012
  • 6. Agenda  Top data center challenges  Distributed (1+N) and central (N+1) static switch  Transformer based and transformer free UPS  Static switches improve MTBF in distribution  Distribution voltage trends and considerations COMPANY CONFIDENTIAL Page 6
  • 7. Top Data Center Challenges External Virtualization, forces Cloud changing the business climate Infrastructure IT Outsourcing Consolidation Management Heat Density Efficiency & Regulation Facility Compliance Green Availability initiatives Challenges Energy Efficiency Higher Increasing Density Demand Power Density Reduced Business & Budget Source: Data Center Users’ Group technology Survey forces pressing on the data center COMPANY CONFIDENTIAL Page 7
  • 8. Top Data Center Manager Concerns Rank Spring 2005 Fall 2007 Spring 2008 Spring 2009 Fall 2009 Spring 2010 Spring 2011 Monitoring Heat Density Heat Density Heat Density Heat Density Availability Infrastructure Availability 1 78% 64% 56% 55% 56% Mgt 53% 51% Monitoring Monitoring Power Power Power Energy Infrastructure Heat Density Infrastructure 2 Density Density Density Efficiency Mgt 49% Mgt 64% 55% 50% 47% 49% 52% Monitoring Energy Availability Availability Infrastructure Heat Density Availability Heat Density 3 Efficiency 57% 45% Mgt 46% 47% 47% 39% 46% Monitoring Space Energy Energy Energy Availability Infrastructure Availability 4 Constraints Efficiency Efficiency Efficiency 33% Mgt 41% 32% 40% 44% 44% 43% Change Space Energy Power Power Power Power 5 Management Constraints Efficiency Density Density Density Density 28% 29% 40% 35% 25% 36% 29% Monitoring Monitoring Space Space Space Space Space Infrastructure Infrastructure 6 Constraints Constraints Constraints Constraints Constraints Mgt Mgt 26% 29% 25% 21% 18% 18% 27% Monitoring / Infrastructure Management properly balances the needs of efficiency and availability Data Center Users’ Group Survey COMPANY CONFIDENTIAL Page 8
  • 9. Liebert AC Power Trends and Strategies Trend Liebert Solution  Liebert APM High-Efficiency  Liebert NX Products  Liebert NXL Energy  Softscale Efficiency Features Improving  Intelligent Eco Modes Efficiency  TP1 (Energy Star) Rated Distribution Transformers  Distribution Voltages (240/139 and 415/240V) Services  Data Center Power & Cooling Assessments  2 Stage (Segmented) Distribution  400A Panel Boards w/ 100% Rated Mains Increased Increasing Power  Busway Solutions Density Requirements  MPX – up to 60A Rack PDU  575V NXL Partnerships &  Universal Switchgear Program System Marketing Materials  Large Systems Design Guide Focus  Development of 1+N for Large Systems High Availability Topologies  Modular Systems with Internal Redundancy Existing Products  Flywheel Systems Renewable  Alternative Energy Storage Energy  Solar – ENPC: Solar Controller, EP: Solar New Products Inverter; DOE Funded Smart Grid Research  Wind – ENPC: Wind Converter COMPANY CONFIDENTIAL Page 9
  • 10. High Availability Configurations 50% UPS 1 UPS 2 UPS 3 UPS 4 50% UPS 1 UPS 2 UPS 3 UPS 4 Utilization Utilization STS STS STS STS STS STS STS STS PDU PDU PDU PDU PDU PDU PDU PDU Interleaved Dual Bus Dual Corded Dual Bus Does not require complex switchgear Requires custom switchgear for power tie STS does the power tie Maximum Loading N/2 Maximum Loading N/2 For 4x1000 kVA=2000 kVA Max Load For 4x1000 kVA=2000 kVA Max Load 66% UPS 1 UPS 2 UPS 3 75% UPS 1 UPS 2 UPS 3 Reserve Utilization Utilization STS STS STS STS STS STS STS STS STS PDU PDU PDU PDU PDU PDU PDU PDU PDU Ring Dual Bus (Distributed Reserve) Reserve/Catcher Dual Bus Does not require complex switchgear Does not require complex switchgear STS does the power tie STS does the power tie Maximum Loading (N-1)/N Maximum Loading N-R For 4x1000 kVA=3000 kVA Max Load For 4x1000 kVA=3000 kVA Max Load COMPANY CONFIDENTIAL Page 10
  • 11. Options for parallel redundant UPS UPS UPS UPS Core Core UPS UPS UPS Core Core Core Core STS SS SS SS Paralleling Cabinet System Control Cabinet IT Load IT Load Distributed Bypass (1+N) Central Bypass (N+1) Distributed static switches Centralized static transfer switch Individual modules manage load transfers System-level control, fault tolerant Cannot parallel different sized UPS Size of STS determines total capacity COMPANY CONFIDENTIAL Page 11
  • 12. N+1 vs 1+N  For a system of 4x750kVA – 1+N will cost $1.2M , max aic 100kaic – N+1 will cost $1.4M , max aic 200kaic – If specifications allow both the 1+N will always be cheaper  When operating on inverter both have identical performance – N+1 has better fault transfer to bypass due to one 3000/4000amp breaker – 1+N has more sag due to parallel SS/inductors/1200a CB during fault transfer. – Since MTBF of NXL module is 200,000 hours the 4 module system will transfer to bypass every 50,000 hr or 6 years if capacity and statistically never if redundant  1+N since it is composed of SMS can easily be split and sent to different locations – Requires two upstream feeder breakers or single input kit versus one for N+1  NEC70E requires both to have downstream ROB to be able to service one module while system is energized COMPANY CONFIDENTIAL Page 12
  • 13. Transformer Based UPS System Single Module, Topology Three-Line AC Output FBO MBB BIB Bypass can be connected to EG MIB separate utility source Input 12P isolated Isolation 3P A BFB AC CB1 FBO E Trap Disconnect CB2 N N MBJ EG or Neutral-Gnd 12P non isolated Output GEC Management; Battery and To Batteries Isolation Low Common DC Bus Mode Noise; Isolation Positive DC bus + + + Separately Derived Source + + + Output -AC Negative DC bus COMPANY CONFIDENTIAL Page 13
  • 14. Transformer Less UPS System Single Module, Topology Three-Line Some topologies require the Less Eff High bypass to be connected to Rectifier DC Bus the same utility source No Output Isolation No Input Additional DC Neutral Mgt / Isolation Converter Control Required COMPANY CONFIDENTIAL Page 14
  • 15. Application Philosophy Transformer Based & Transformer Free UPS  There are appropriate applications for both transformer based and transformer free UPS – Many customers have multiple applications with different priorities  Transformer based enterprise UPS’s offer the highest availability – Galvanic isolation is provided for DC fault protection – Output isolation protects the critical load and simplifies fault management – Use ultra-reliable, efficient SCR-based rectifiers and simple lower voltage inverters – Can feed rectifier and bypass from dual Separately Derived Sources – Inherently compatible with High Resistance Grounded systems  Transformer-free UPS’s offer low TCO with high availability – Double conversion efficiency up to 96% – Uniformly Low input harmonics with consistent high power factor. – Power distribution provides complete solution for transformer free UPS COMPANY CONFIDENTIAL Page 15
  • 16. Transformer Based –vs- Transformer Free Design Characteristic Transformer Free Transformer Based AC-AC Double Conversion Efficiency 96% Range 94% Range Eco Mode Efficiency Up to 99% Up to 99% Ground Fault Protection Coordination External or Incremental Inherent Arc Flash Mitigation External or Incremental Inherent > 480 volt ratings for high power Additional External No Additional External density Xformers Required Xformers Needed Reduction in Common mode noise No Yes and EMI Rectifier Resiliency IGBT vs. SCR Lower Higher High Resistance Ground No Yes Compatibility COMPANY CONFIDENTIAL Page 16
  • 17. System MTBF Without Static Switches Module Demonstrated MTBF Block Diagram Tier 3-4 UPS Power configuration into a Dual Input IT Load MTBF UPS Out = UPS 1 = UPS2 Primary AC Input MTBF = S10 UPS MTBF out = > 1.6M hr MTBF Field Observed Bypass AC Input = 100 Hr MTBF Bypass AC Input PDU MTBF > 9 M hr UPS 1 Field-Observed Primary AC Input SMS MTBF > 1.7 M hr PDU IT each AC Input MTBF = Simplified - Components in series = 1/((1/MTBF UPS) + (1/MTBF PDU)) IT Load MTBF = 1.4 M hr Primary AC Input PDU UPS 2 Bypass AC Input SMS COMPANY CONFIDENTIAL Page 17
  • 18. System MTBF Improvement With Static Switches Module Demonstrated MTBF Block Diagram Tier 3-4 UPS Power configuration with STS 2 into a Dual Input IT Load MTBF UPS Out = UPS 1 = UPS2 Primary AC Input MTBF = S10 UPS MTBF out = > 1.6M hr MTBF Field Observed Bypass AC Input = 100 Hr MTBF Bypass AC Input STS MTBF > 7.2 M hr PDU MTBF > 9 M hr UPS 1 MTBF > 1.7 M hr Field-Observed Primary AC Input SMS STS2 PDU enter UPS MTBF = 1.7 Combined MTBF of two STS 2 Field-Observed MTBF: Paralleled UPS outputs Field-observed STS MTFB output = MTBF1+MTBF2+((MTBF1*MTBF2)/(MTTR)) ≈ 7.2 M hr MTBF IT Load MTBF = 113,441 M hr IT each AC Input MTBF = Simplified - Components in series where Mean Time to Repair [MTTR] = 24 hrs = 1/((1/Para UPS Out) + 1/MTBF STS) + (1/MTBF PDU)) where UPS repair is less than 8 hrs enter MTBF = 4.0 M hr Primary AC Input STS2 PDU UPS 2 Bypass AC Input SMS COMPANY CONFIDENTIAL Page 18
  • 19. Traditional Dual Bus, 2N Precision Engine Cooling Generators Generator Feed to Service Surge Input Paralleling Feed Suppression Switchgear Switchgear UPS UPS A Primary Alternate STS2 STS2 LBS PDU: RDC/ RDC/ Alternate Racks PDU: Primary PPC/FPC FDC FDC PPC/FPC Multiple Rows UPS B Dual Bus = twice as many power cables COMPANY CONFIDENTIAL Page 19
  • 20. Distribution Voltages 600VAC •UPS 600V •PDU 208/120V •Rack 480VAC •UPS 480V •PDU 208/120V •Rack Today 415VAC •UPS 415/240V •RDC 415/240V •Rack 480VAC •UPS 480/277V •RDC 480/277V •Rack 600VAC •UPS 600V •PDU 415V •Rack Emerging 480VAC •UPS 415/240V •RDC 415/240V •Rack Efficiency improvement ??? COMPANY CONFIDENTIAL Page 20
  • 21. Isolation Transformers At The PDU PROS  Single point ground, separately derived source with safety ground closer to the load reduces susceptibility to lightning and other transients  Only requires a 3 wire system to the PDU input  Provide impedance which reduces available fault currents ~ and Arc Flash potential at distribution points CONS  Size – PDU’s with transformers can be larger  Transformation losses …However…today’s TP-1 transformers are typically 98.5% + efficient  Higher weight and cost COMPANY CONFIDENTIAL Page 21
  • 22. PDU Transformer Efficiency 99.00 $$$ 98.50 % EFFICIENCY 98.00 300 kVA K20 300 kVA STD 97.50 300 kVA K20 TP1 97.00 300 kVA STD TP1 96.50 96.00 15% 25% 35% 50% 65% 75% 100% % LOAD COMPANY CONFIDENTIAL Page 22
  • 23. A Fresh Look at the 400-415v System  Modern Power supplies are wide ranging 208v to 240v test – Higher voltage equates to higher efficiency – about 0.3% gain  Line to neutral connection – 230/400 or 240/415v – Can be transformer free saving energy-1-3% gain, plus cooling savings – Fault current HAS been a major concern if transformer free • 480 or 600v to 240/415 v with Auto (efficiency) or Iso. (aic and N-G) • Historically, vendors supplied pieces and parts, but not an end-to- end solution for 400-415V in North America. – Neutral fault path and neutral noise are concerns with transformer free – No Rack PRU balancing issue  Line to Line connection – 120/208 and 127/240v – New copper TP-1 Transformers have 1.5% losses – Fault current is controlled by the transformer • Panels, breakers, power cords, rack PDU and servers rated for fault current (aic) are readily available – Neutral fault path and neutral noise are from server to isolation transformer only COMPANY CONFIDENTIAL Page 23
  • 24. Short Circuit Considerations (Historical) Panelboards  208/120 & 240/139 Volt Panels Rated at 250V – Type NQ – Available to 22kAIC  480/277 & 415/240 Requires Panels Rated to 600V – Type NF – Series rated with main CB at • 35,65 and 100kaic – Physically larger – More costly (10-25%) Are your Rack PDUs and servers rated for this high AIC? COMPANY CONFIDENTIAL Page 24
  • 25. Fault Current Arc Flash Considerations  Arc flash? – Bolted vs. arcing faults – Significant incident energy released during the arcing event and is considered the “arc flash hazard”  NFPA 70E-2004 “A flash hazard analysis be done in order to protect personnel from the possibility of being injured by an arc flash”  Determination of required PPE - Personal Protective Equipment  Calculation of incidence of energy – Ampere rating of over current protective device – Operating time of the device – Available fault current is key!!! COMPANY CONFIDENTIAL Page 25
  • 26. Solving the 415V AIC Issue Problem 3250 kVA 3250 kVA • AC Distribution panels 34.5 kV – 34.5 kV – • Lighting panels 480/277 415/240 Z >= 5.32% X Z >= 5.32% X • Exposed buss (arch flash) Isc ~ 73,480A Isc ~ 84,989A • AIC of UL approved “touch safe” • Rack PDUs UPS UPS • AIC may exceed safe design SYSTEM SYSTEM Solutions • Introduce impedance such as inductor or transformer •Disadvantage efficiency •Advantage grounding and fault management (tx) • I-Line Panels offer higher AIC 300 kVA 480V – (100k) and safer design 208/120V PDU PDU • Higher AIC capable RPDU’s Z >= 4% X X Isc ~ 17,576 A Isc ~ 56,144 A RACK RACK Isc < 5kA Isc ~ 10-12kA 208 Volt 415 Volt Distribution Distribution COMPANY CONFIDENTIAL Page 26
  • 27. Distribution Voltage Considerations UPS System Voltage and Capacity 5000 Amp System UPS System Voltage 415V 480V 600V Max. Bus Capacity 3590 kVA 4152 kVA 5190 kVA  Maximize your investment in breakers and gear with higher UPS System voltages  The higher the chosen voltage - the greater the potential capacity – 15% to 25% COMPANY CONFIDENTIAL Page 27
  • 28. Distribution Voltage Pros & Cons PROS CONS  Most commonly accepted application  2-3% transformation energy loss 480 – 208/120  Reduced aic – fault curent  208V requires 2 pole breaker  Uses standard 240V panelboard & breakers  Reduces the number of poles 600 – 208/120  N-G bond at PDU  N-G bond at PDU( iso)  0.5 to 1.3%% transformer energy loss 480 – 400/230  Higher energy efficiency  Can’t power 120V equipment  Higher energy density  More circuits due to1-pole 600 – 400/230  Higher UPS capacity - kVA  N-G bond (auto) at service entrance  Reduced AIC – fault current  No transformation energy losses  Can’t power 120V or 240V equipment 480 – 480  No neutral required (unless 277V loads)  Requires 480V panelboard & breakers  Few servers at 480V & 277V 480 – 480/277  Higher AIC – fault current at load  No transformation energy losses  N-G bond at bypass transformer  240V load requires 1 pole breaker  Requires 480V panelboard& breakers 480 – 415/240  More useable pole spaces  Requires UPS Maint Bypass Xfmr  Higher energy efficiency  Higher AIC – fault current at load  No transformation energy losses  Can’t power 120V equipment  Reduced cooling load  Requires 480V panelboard& breakers  240V load requires 1 pole breaker  Needs different approach to fault 415 – 415/240  More useable pole spaces current management  Higher energy efficiency  N-G bond at service entrance  Save cost and weight of transformers in  Increase cost of full neutral and higher PDUs ampacity – lower system kVA COMPANY CONFIDENTIAL Page 28
  • 29. 29 COMPANY CONFIDENTIAL Page 29 29
  • 30. Liebert STS2, S610, NXb, PPC, FPC, NXL Reliability Summary May 2011 Product Operating Hours Mod. MTBF Sys. MTBF (Cur # Units) Oct 00 – Mar 11 Code 14 Code 15 Transfer To Bypass Unfiltered Filtered Critical Bus Failure STS 2 (4,082) 121,462,656 Hrs. 886,589 Hrs. 8,675,904 Hrs. S610 (6,642) 419,488,584 Hrs. 47,838 Hrs. 1,712,198 Hrs. NXb (2,843) 105,092,280 Hrs. 202,490 Hrs. 2,563,226 Hrs. PPC (10,474) 878,674,536 Hrs. 2,670,743 Hrs. 10,217,146 Hrs. FPC (1,951) 41,363,976 Hrs. 10,340,994 Hrs. 13,787,992 Hrs. NXL (612) 5,581,704 Hrs. 206,730 Hrs. 1,395,426 Hrs.* APM (113) 384,432 Hrs. 384,432 Hrs. 384,432 Hrs. * Updated Nov 2011 COMPANY CONFIDENTIAL Page 30 30
  • 31. Power Business Segments Primary Motivation Critical TCO Infrastructure Availability Capital/Operational Savings Capital/Operational Savings Availability Core Enterprise Scale-Out Customer Traditionalist Opportunist Experimentalist Type Operates on the edge of Firmly adheres to long-held, Ventures outside of industry Customer acceptable operating proven industry standards to standards and best-practices Behavior & recommendations taking maximize infrastructure with the goal to significantly Motivation calculated risks to balance availability reduce financial costs financial costs and availability Primary Transformer Based Transformer Based Transformer Free Battery on Server Technology UPS UPS in Eco-Mode UPS in Eco-Mode Model Transformer Free UPS • Providing mission critical • Providing less critical • Customers still expect computing to customers computing to internal or application high availability • Required uptime based on external customers • Basic services are provided Customer government regulations • Need to meet customer SLAs for limited fees with no Attributes • Extremely high cost of for uptime with limited guarantees application downtime penalties • High compute volume • Balancing cost of downtime demands lowest computing with OPEX costs possible COMPANY CONFIDENTIAL Page 31
  • 32. High Availability Configurations 50% UPS 1 UPS 2 UPS 3 UPS 4 50% UPS 1 UPS 2 UPS 3 UPS 4 Utilization Utilization STS STS STS STS STS STS STS STS PDU PDU PDU PDU PDU PDU PDU PDU Interleaved Dual Bus Dual Corded Dual Bus Does not require complex switchgear Requires custom switchgear for power tie STS does the power tie Maximum Loading N/2 Maximum Loading N/2 For 4x1000 kVA=2000 kVA Max Load For 4x1000 kVA=2000 kVA Max Load 66% UPS 1 UPS 2 UPS 3 75% UPS 1 UPS 2 UPS 3 Reserve Utilization Utilization STS STS STS STS STS STS STS STS STS PDU PDU PDU PDU PDU PDU PDU PDU PDU Ring Dual Bus (Distributed Reserve) Reserve/Catcher Dual Bus Does not require complex switchgear Does not require complex switchgear STS does the power tie STS does the power tie Maximum Loading (N-1)/N Maximum Loading N-R For 4x1000 kVA=3000 kVA Max Load For 4x1000 kVA=3000 kVA Max Load COMPANY CONFIDENTIAL Page 32
  • 34. User Spotlight: Donna Manley Post mortem procedures
  • 35. Managing a Full Data Center Power Down Donna M. Manley, MBA IT Senior Director, Computer Operations University of Pennsylvania
  • 40. 40
  • 41. Before you get started…. • Agree upon scope • Documentation • Validate infrastructure and architecture • Asset identification and application dependencies • Understand what pre-work can be completed • DR site and Vital Records storage providers on standby • What’s the weather forecast? Take the opportunity to do stuff you wouldn’t normally be able to without an outage! 41
  • 42. 42
  • 43. 43
  • 44. 44
  • 45. Logistics…. • Coordination with Public Safety • Coordination with Facilities • Command Center • Know who will be there and when • Vendor Expectations • Accommodations, food, and beverage 45
  • 46. 46
  • 47. 47
  • 48. Managing the Outage… • Communication (Bridges, Web, Email) • Playbook • Change Freeze • Action Items to be remediated prior • Test plan • Points of Contact - Data Center/Facilities/Vendors • Who gives the “GO” 48
  • 49. 49
  • 50. 50
  • 51. 51
  • 52. Post Outage… • Communication (Bridges, Web, Email) • Execute Test Plan • Lessons Learned • Process and procedural modifications • Automation opportunities • Sleep! Lots of great information was compiled for this event – keep it current! 52
  • 53. Thank you for allowing me to share my thoughts with you today! Donna M. Manley, MBA IT Sr. Director, Computer Operations ITIL V3 Foundations Certified University of Pennsylvania manleydm@isc.upenn.edu 53
  • 54. Survey – Was this forum beneficial? – Was this the proper number of end users or should the forum grow? If grow, please give a number you feel would be appropriate. – How often should this forum meet? When? – What topics would you be interested in discussing at the next meeting? – What other venues for this event would you like to see?
  • 55. Thank you for attending!

Hinweis der Redaktion

  1. An interesting dynamic in our research has been the ascension of Infrastructure Management and Monitoring as a top of mind concern to data center managers. The reason behind this dynamic is the acknowledgment of users that a gap exists in our ability to properly balance the needs of availability and efficiency and management tools can fill this gap. Data centers operate as an eco-system and is measured as a system, thus, the management tool(s) must be able to view and manage the holistic data center environment, not just the individual pieces and parts.
  2. Here are the most common redundant UPS configurationsOne is referred to as N+1: N modules plus 1 central static switchThe other is referred to as 1+N: 1+1+1+ modules to N with a distributed static switchEach has its strengths and optimum applicationsA white paper is available with those details
  3. Subject: Advantages of a transformer based UPS over a transformer-less design: PW9395 vs. NXL or S610There are important advantages of a transformer based UPS over a transformer-less design:UPS DC Bus design- Transformer-less UPS 480V in/out systems must create as a minimum a (+) AND (-) 400VDC bus.  If a fault occurs then there is the potential for 800VDC to propagate downstream to critical load equipment (servers).- Transformer-based systems use a lower more manageable DC bus, typically 540VDC.  This allows the rectifier to charge the batteries directly (batteries connected across DC bus for more efficient dual conversion), and if a fault occurs the isolation transformers will not allow DC to pass upstream or downstream of the UPS module.  Therefore, the DC fault will be contained within the UPS system itself and not propagate into the building infrastructure or data center.  With a With a transformer-less UPS design an isolation transformer located on the input and output of the UPS is recommended.Two separate input AC sources for higher reliability and maintainability- Transformer-less systems violate isolation between dual input AC sources when the transformer-less system’s rectifier is fed from one AC source and the system’s bypass is fed from a second AC source.  If a UPS fault occurs in this case the two AC sources will be connect together via the fault, which violates the fault isolation goal and compartmentalization, hence a code violation.  For this reason a Transformer-less UPS system must be fed from the same AC source, aka, single input feed.- Transformer-based systems have an output transformer and the bypass is connected on the load side (secondary-side) of the output transformer.  If a UPS fault occurs in this type of system the two AC sources are isolated via the isolation transformer.  The fault is isolated and compartmentalization is maintained.  The advantage of a Transformer-based system is the UPS rectifier and the UPS bypass can be fed from two different sources (i.e., utility and engine generator) providing higher reliability and serviceability. Pulse paralleling advantages with two separate input AC sources  - Liebert designs UPS systems to be able to run the bypass in parallel with the inverter in cases of extreme overloads or to clear a downstream fault.  During this mode or during a standard transfer to bypass of a UPS system (make-before-break) a transformer-based system maintains utility isolation via its isolation transformer.  Again there is an advantage to separate the AC inputs to the rectifier and bypass for higher reliability and serviceability. - Transformer-less system in this example is in essence connecting the two utilities together via the UPS power train, which is a code violation.Other significant benefits for the use of transformer-based UPS systems in enterprise applications- A transformer-based UPS can be used to create and maintain a separately derived source, meaning poor grounding and long neutral conductors are eliminated.  - Common mode noise/voltages are significantly reduced via isolation. - Safety and noise grounding and references all the way back at the service entrance especially with switched neutrals are maintained. - Better ground fault protection/coordination with transformer-based UPS.- Higher arc flash energy of faulted transformer-less systems will be evident.- An input isolation transformer-based UPS provides better personnel safety for open rack battery applications.  Liebert produces both transformer-based and transformer-less UPS systems.  Our recommendation as validated by applications and consultants across the US is to continue to provide transformer-based UPS systems for enterprise applications.